SECTION 1001
SECTION 1002
SECTION 1003
SECTION 1004
-
Location. The location and layout of the fire command center shall be approved by the department. A plan identifying the proposed location and layout of the fire command center, including the location, model and certificate of approval number of the fire alarm system control panel, shall be submitted to the department for approval prior to installation.
-
Fire alarm system control panel. The fire alarm system control panel shall be of a type for which a certificate of approval has been issued, and shall be installed in accordance with this code.
- Maintenance. The fire alarm system control panel shall be maintained in accordance with this code.
SECTION 1005
- Protective covers. The Fire Chief and the Chief Fire Marshal may require the installation of manual fire alarm box protective covers to prevent malicious false alarms or provide the manual fire alarm box with protection from physical damage. The protective cover shall comply with the requirements of the construction codes including this code.
SECTION 1006
SECTION 1007
SECTION 1008
SECTION 1009
- Exception: Central station monitoring is not required for: Single- and multiple-station.
SECTION 1010
SECTION 1011
SECTION 1012
SECTION 1013
SECTION 1014
-
Testing. Testing shall be performed in accordance with the schedules or more frequently where required by the Fire Chief or Chief Fire Marshal.
- Exception: Devices or equipment that are inaccessible for safety considerations shall be tested during scheduled shutdowns where approved by the fire chief or the chief fire marshal, but not less than every 18 months.
Report Code